I have two new construction smaller residential homes on a single site that the owner wants to backup using a single generator placed in between them. Normally when I feed two structures from a generator, its for a commercial project and I usually just call out for the generator to have two circuit breakers. However, being that this is more of a residential style generator, im not sure I have that option.
The generator they want to use is a Kohler (60RCL) which comes with a 250A circuit breaker. My plan was to set a MLO 400A rated panel (Panel GDP) next to the generator and then put a 150A circuit breaker and a 125A circuit breaker within that panel (one for each respective structure). The panel would be mounted on a concrete pedestal.
With respect to grounding, do I treat the pedestal like a separate structure? So I would have a GEC at the panel to driven ground rods, and then I would have an EGC routed with the feeder conductors to each respective SER ATS where I would then have an additional GEC? Then im assuming there would just be an EGC between the generator and the generator distribution panel (GDP?
The generator they want to use is a Kohler (60RCL) which comes with a 250A circuit breaker. My plan was to set a MLO 400A rated panel (Panel GDP) next to the generator and then put a 150A circuit breaker and a 125A circuit breaker within that panel (one for each respective structure). The panel would be mounted on a concrete pedestal.
With respect to grounding, do I treat the pedestal like a separate structure? So I would have a GEC at the panel to driven ground rods, and then I would have an EGC routed with the feeder conductors to each respective SER ATS where I would then have an additional GEC? Then im assuming there would just be an EGC between the generator and the generator distribution panel (GDP?