I am mostly a residential electrician that does not have much experience with motors, so apologies if I am asking a silly question.
I have a job for a family member (oh those jobs are fun LOL). It is in a two room office space that has two seperate main lug subpanels located in room #1 with a 3 phase 4 wire 120/120/208 volt service. One panel is a 100 amp single phase currently feeding lighting/outlets and AC/furnace. The second panel (which is currently not being used for any circuits) is a 100 amp 3 phase service. Both panels are being fed from the main electrical room located elsewhere in the building.
Room #2 will now need power to a new 3 phase 208 volt 10 HP motor feeding a large air compressor. The motor & compressor are installed in an existing enclosure/housing which has an existing start & stop control and an existing magnetic starter with overload protection.
I understand the motor calculations for circuit conductor size, short-circuit and ground-fault protection, and overload protection as well as when to use the NEC vs the nameplate for calculations. I also understand that since the panel with the circuit breaker and the motor are in different rooms, a disconnect will be required within sight of the motor.
My question: does this disconnect need to be fused or non-fused (safety switch) per NEC 2011? I just cannot seem to figure that one out LOL.
Thank you for any suggestions or guidance to code references.
(Today was the first day I came across this forum and I must say what a great resource of information and ideas.)
I have a job for a family member (oh those jobs are fun LOL). It is in a two room office space that has two seperate main lug subpanels located in room #1 with a 3 phase 4 wire 120/120/208 volt service. One panel is a 100 amp single phase currently feeding lighting/outlets and AC/furnace. The second panel (which is currently not being used for any circuits) is a 100 amp 3 phase service. Both panels are being fed from the main electrical room located elsewhere in the building.
Room #2 will now need power to a new 3 phase 208 volt 10 HP motor feeding a large air compressor. The motor & compressor are installed in an existing enclosure/housing which has an existing start & stop control and an existing magnetic starter with overload protection.
I understand the motor calculations for circuit conductor size, short-circuit and ground-fault protection, and overload protection as well as when to use the NEC vs the nameplate for calculations. I also understand that since the panel with the circuit breaker and the motor are in different rooms, a disconnect will be required within sight of the motor.
My question: does this disconnect need to be fused or non-fused (safety switch) per NEC 2011? I just cannot seem to figure that one out LOL.
Thank you for any suggestions or guidance to code references.
(Today was the first day I came across this forum and I must say what a great resource of information and ideas.)