Single Motor - Disconnect: Fused or Non-fused?

Status
Not open for further replies.

mrtom

Member
Location
Chicago-Area
I am mostly a residential electrician that does not have much experience with motors, so apologies if I am asking a silly question.

I have a job for a family member (oh those jobs are fun LOL). It is in a two room office space that has two seperate main lug subpanels located in room #1 with a 3 phase 4 wire 120/120/208 volt service. One panel is a 100 amp single phase currently feeding lighting/outlets and AC/furnace. The second panel (which is currently not being used for any circuits) is a 100 amp 3 phase service. Both panels are being fed from the main electrical room located elsewhere in the building.

Room #2 will now need power to a new 3 phase 208 volt 10 HP motor feeding a large air compressor. The motor & compressor are installed in an existing enclosure/housing which has an existing start & stop control and an existing magnetic starter with overload protection.

I understand the motor calculations for circuit conductor size, short-circuit and ground-fault protection, and overload protection as well as when to use the NEC vs the nameplate for calculations. I also understand that since the panel with the circuit breaker and the motor are in different rooms, a disconnect will be required within sight of the motor.

My question: does this disconnect need to be fused or non-fused (safety switch) per NEC 2011? I just cannot seem to figure that one out LOL.

Thank you for any suggestions or guidance to code references.

(Today was the first day I came across this forum and I must say what a great resource of information and ideas.)
 
Unless the compressor has a requirement for "fuse protection", the NEC would accept a non-fuse disconnecting means.
 
Thank you for the reply. I thought that was the case since the motor/compressor has the magentic starter which provides overload protection.......and if the magentic starter was not present, then the fused disconnect would be required(?). I will double check to see if anything states that the compressor needs fused protection. And for a bonus, I believe the safety switch is cheaper LOL.
 
Basically, unless there is some circumstance such as manufacturer requirement or engineering requirement (such as fault current reduction) a fusible disconnect or breaker can be used for short-circuit protection or overload protection. If those issues are addressed then the only need is for a properly rated disconnecting means.

You may find the motor starter requiring fuse protection...some do.
 
Thanks again for the information, it was very helpful. I do believe that the disconnecting means should be rated for the amperage of the circuit AND rated for the HP of the motor. Thanks again. What an excellent forum!
 
...located in room #1 with a 3 phase 4 wire 120/120/208 volt service. ....

Room #2 will now need power to a new 3 phase 208 volt 10 HP motor...
When you say 120/120/208 do you mean that is the voltage from each ungrounded conductor to neutral (or ground)... or is it just a typo and you simply mean 208/120 3? 4W?

The reason I ask is because 120, 208, and 120 are what the voltages would measure to neutral or ground for a 240/120 3? 4W system.
 
Oh my, that was a typo! It is a 208/120 3? 4W service. Thanks for asking, I could see how that could be a major goof-up if someone messed that up on the jobsite LOL.
 
Lets just say a disconnecting means does not require overcurrent protection. If it is desirable or even required to have fuses as overcurrent protection, then a fusible disconnect as this local disconnect is often the most economical way to achieve that.
 