I have a customer he is sensitive to electricity (EMF), we are trying to have a single neutral/ground connection on a pretty complicated system.
Basic Overview:
200 amp main meter supplies a 200 amp SR automatic transfer switch - 3 Wire (Main Disconnect) currently neutral/ground bond- FEEDS MAIN HOUSE PANEL
100 amp meter (line side off main meter-3 wire) to a 100 amp SR automatic transfer switch - FEEDS HEAT PUMP - currently neutral/ground bond
20 KW whole generator -single feed going to 200 amp TS first then to 100 amp TS (four wire, no ground rod, no neutral/ground connection at generator)
6.1 KW stand alone solar array
with microinverters 300 feet behind the house, feeding on load side (Main Panel). Solar array -- Inventor panel (Isolated N/G), ground rod installed at solar array-- 4-wire to AC Disconnect (Grounded Only) --- generation Meter (neutral terminated) --- 4 wire to Main House Panel Load side.
(2) ground rods outside at house
Questions:
Does the 100 amp SR automatic Transfer Switch need a neutral/ground connection, because its a service disconnect? I would like the only Neutral/Ground connection to be at the 200 amp SR transfer switch.
The Solar Array Neutral and Ground is confusing me. They ran 4-wire from the AC Disconnect to the Solar Array system Inventor panel and wired it like a sub panel (Isolated N/G). The meter is a 3-wire termination design, Is that termination a neutral or ground? Can I run the neutral uninterpreted back to the main panel.
The Solar Array feeds into the House Panel, which the house panel is a 4-wire isolated system.
When all is done, the only N/G connection is at the 200 amp SR transfer switch. Grounds rod will terminate here also.
Basic Overview:
200 amp main meter supplies a 200 amp SR automatic transfer switch - 3 Wire (Main Disconnect) currently neutral/ground bond- FEEDS MAIN HOUSE PANEL
100 amp meter (line side off main meter-3 wire) to a 100 amp SR automatic transfer switch - FEEDS HEAT PUMP - currently neutral/ground bond
20 KW whole generator -single feed going to 200 amp TS first then to 100 amp TS (four wire, no ground rod, no neutral/ground connection at generator)
6.1 KW stand alone solar array
with microinverters 300 feet behind the house, feeding on load side (Main Panel). Solar array -- Inventor panel (Isolated N/G), ground rod installed at solar array-- 4-wire to AC Disconnect (Grounded Only) --- generation Meter (neutral terminated) --- 4 wire to Main House Panel Load side.
(2) ground rods outside at house
Questions:
Does the 100 amp SR automatic Transfer Switch need a neutral/ground connection, because its a service disconnect? I would like the only Neutral/Ground connection to be at the 200 amp SR transfer switch.
The Solar Array Neutral and Ground is confusing me. They ran 4-wire from the AC Disconnect to the Solar Array system Inventor panel and wired it like a sub panel (Isolated N/G). The meter is a 3-wire termination design, Is that termination a neutral or ground? Can I run the neutral uninterpreted back to the main panel.
The Solar Array feeds into the House Panel, which the house panel is a 4-wire isolated system.
When all is done, the only N/G connection is at the 200 amp SR transfer switch. Grounds rod will terminate here also.