Homeowner is removing a hot tub and wants me to use the existing 40-amp feeder 3#8s and a #10 insulated ground and mount a 3R subpanel on a post where the hot tub was.
Reading 215.9 It looks like GFCI can be the feeder breaker in the house or the branch circuit breakers in the outdoor sub.....is that correct? No requirement for the feeder itself to be GFCI protected?
My only other question is does this require a ground rod?
If 250.32 and the exception says what I think it does it needs one because they would allow a multi wire circuit to run out there without a ground rod if it was a branch circuit but not if it's a feeder.
Do I have that right?