On a recent installation of a single phase 400 amp with standard ringless meter base going to two. 200A disconnects each going to 200 amp main lug panels. The state inspector filled it, because the phase were wired on opposite sides of the breaker on each disconnect. Exact memo on permit; “meter base and disconnects not properly wired (a phase to one panel, b phase to other panel)”
My interpretation
So the electrician that wired it wired the first phase to the left side and second phase to the right side of first disconnect breaker and the first phase to the right side and the second phase to the left side of the second disconnect breaker.
Definitely not attention to detail and not perfect. I am putting this on here to ask anybody’s thoughts on this; safety concerns? Functionality (Does it work?), or any other comments.
My interpretation
So the electrician that wired it wired the first phase to the left side and second phase to the right side of first disconnect breaker and the first phase to the right side and the second phase to the left side of the second disconnect breaker.
Definitely not attention to detail and not perfect. I am putting this on here to ask anybody’s thoughts on this; safety concerns? Functionality (Does it work?), or any other comments.