Single phase and three phase transformer L-L full load current calculation shortcuts.

Status
Not open for further replies.

11bgrunt

Pragmatist
Location
TEXAS
Occupation
Electric Utility Reliability Coordinator
Shortcuts that have always worked for me.
Single phase and three phase transformer L-L full load current calculation shortcuts. Examples of my shortcut and the actual calculation results are below.


1Phase @ 240 L-L Volts = kVA X 4
100kVA X 4= 400 vs 416.7 Amps

3Phase @ 208 L-L Volts = kVA X 2.8
1000kVA X 2.8 = 2,800 vs 2,775.8 Amps

3Phase @ 240 L-L Volts = kVA X 2.4
1000kVA X 2.4 = 2,400 vs 2,405.7 Amps

3Phase @ 480 L-L Volts = kVA X 1.2
1000kVA X 1.2 = 1,200 vs 1,202.8 Amps
 