This may seem elementry but I need the refresher. A 200KW 50Hz (415/240)generator @ .8 PF supplies 3 phase power. For a three-phase load my generator is capable of suppling the following amperage:
200kw / 415*1.73*.8 = 348amps
For single phase loads each leg can supply
200kw / 240*.8 = 1041 amps
Is this 1041 amps per leg A-N, B-N, and C-N or 348 amps A-N, B-N, and C-N
Thanks in advance for the clarification
200kw / 415*1.73*.8 = 348amps
For single phase loads each leg can supply
200kw / 240*.8 = 1041 amps
Is this 1041 amps per leg A-N, B-N, and C-N or 348 amps A-N, B-N, and C-N
Thanks in advance for the clarification