Hey there. I'm studying for my Master's Exam and reviewing my Mike Holt course. The example question says. What's the demand load for twenty single- phase 14 kw 208v ranges on a three- phase service? My question is how do they come up with 7 ? Divide 20 units by the 3 phases ? Thank you.

Sent from my Moto G (4) using Tapatalk
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Hey there. I'm studying for my Master's Exam and reviewing my Mike Holt course. The example question says. What's the demand load for twenty single- phase 14 kw 208v ranges on a three- phase service? My question is how do they come up with 7 ? Divide 20 units by the 3 phases ? Thank you.

Sent from my Moto G (4) using Tapatalk

14 kw * 21 ranges is 280 kw or about 816 Amps per phase

I don't know where they came up with seven either.
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
Hey there. I'm studying for my Master's Exam and reviewing my Mike Holt course. The example question says. What's the demand load for twenty single- phase 14 kw 208v ranges on a three- phase service? My question is how do they come up with 7 ? Divide 20 units by the 3 phases ? Thank you.

Sent from my Moto G (4) using Tapatalk

7 would be the maximum number of ranges connected between any two phases (Yes, divide 20 by 3, and round up). The calculation would be based on twice that, or 14 ranges.
 
Last edited:

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
the Op said the answer given was "7". I have no idea where that came from.

I don't think 7 was the answer given, I think 7 was part of the process to get the answer, but the OP didn't know how they got the 7.
At least that is what I got from his question.
 
Out of curiosity, what is the answer in the review course?
The answer is 48 kw. Step 1: determine the maximum number of ranges between any two phases: 7 units. Step 2: Apply table 220.55 demand for twice the maximum number of ranges between any two phases: 7 units x 2= 14 units: 29kw. 14 kw range exceeds 12 kw by 2 kw. Increase the c column 29 kw by 5% for each kw in excess of 12 kw. Demand load =29 kw x1.10. Demand load =32 kw. Step 3: Demand load per phase: 32 kw/2 phases= 16 kw. Demand load for three phases= 16 kW x 3. Demand Load for three Phases= 48 KW.

Sent from my Moto G (4) using Tapatalk
 