I'm in an industrial setting. To comply with OHSA/NEC/NFPA, we like to have a lockable disconnect on any piece of equipment. Historically, most everything is 3-phase, and we'd just install a 3-phase, fused, lockable disconnect next to the machine.
We've got a single phase 120VAC boiler going in, and I expected the install would be similar, but I'm running into some questions:
- I know that according to NEC 240.22 we aren't supposed to fuse the neutral. Exceptions for 240.22 are when the overcurrent device opens all conductors in the circuit (which would not be true of a fuse), and in cases where it is required for motor overcurrent protection (this would be power to a control circuit and also a motor, the motor having it's own overcurrent protection, so I don't believe this applies).
- I understand that the disconnect device required for LOTO does not have to be fused, it's just typically this way on 3-phase for convenience.
I've checked a couple electrical suppliers, but I'm having a lot of trouble finding a single phase lockable disconnect. There are plenty of 2 pole disconnects where both poles are fused (would these be allowed?). I've seen others use what appears to be a light switch on the hot leg (compared to a typical three phase disconnect with a big pull handle, those seem suspicious to me).
What is the best practice when installing a disconnect device on a single phase circuit?
We've got a single phase 120VAC boiler going in, and I expected the install would be similar, but I'm running into some questions:
- I know that according to NEC 240.22 we aren't supposed to fuse the neutral. Exceptions for 240.22 are when the overcurrent device opens all conductors in the circuit (which would not be true of a fuse), and in cases where it is required for motor overcurrent protection (this would be power to a control circuit and also a motor, the motor having it's own overcurrent protection, so I don't believe this applies).
- I understand that the disconnect device required for LOTO does not have to be fused, it's just typically this way on 3-phase for convenience.
I've checked a couple electrical suppliers, but I'm having a lot of trouble finding a single phase lockable disconnect. There are plenty of 2 pole disconnects where both poles are fused (would these be allowed?). I've seen others use what appears to be a light switch on the hot leg (compared to a typical three phase disconnect with a big pull handle, those seem suspicious to me).
What is the best practice when installing a disconnect device on a single phase circuit?