I know that the engineering firm I work for recently designed a building at 208Y/120V-3ph with a single 120/240V-1ph (technically 120/208V-1ph) panel served from a single phase transfer switch and 120/240V generator. This was due to the client wanting to utilize a generator to provide power for several small medical refrigerators. We did not have any AHJ issues, just issues regarding the ATS. There was concern that the ATS originally submitted for review would never switch back from generator to normal power. This was due to the 240V ATS not sensing a sufficiently high voltage on the normal utility. The supplier went to a slightly more expensive but infinitely more adjustable ATS to allow the setpoints to be set for the 208V normal service.