goldstar
Senior Member
- Location
- New Jersey
- Occupation
- Electrical Contractor
I recently came across this situation where another electrical contractor installed a 240 volt, single phase GFCI circuit breaker for a pool motor on a 240V, 3-phase Delta breaker panel. There were 2 other pool motors attached to this panel but purely by coincidence the breakers for those pools landed on phases 1 & 3 and were working fine. When the CH-tan handle 2-pole, 20A GFCI breaker for the pool heater was installed in the panel it landed on phases 1 & 2. Needless to say, the breaker blew up. The reason - phase 1 measures 120V to ground but phase 2 measures about 200V to ground. I'm just posting this for anyone else who might run into this problem.