Customer has 2 gas compressors at a remote station that only has a 120/240V single phase service. One motor is 10HP and the other is 15HP. The customer prefers Powerflex 525 drives, but in order to run the drive on a single phase input, we have to derate the drive by 65%, so the 10HP motor would require a 15-20HP drive, and the 15HP motor would require a 25HP drive. Is that correct?
If so, I would most likely recommend that the customer step up to a Powerflex 755 drive, which is available in both 20HP and 25HP ratings, for 240VAC input.
I suppose the alternative would be using a rotary phase converter in order to stick with the cheaper drive (PF525), but I really don't think there'd be any cost savings, plus now there's another failure point.
If so, I would most likely recommend that the customer step up to a Powerflex 755 drive, which is available in both 20HP and 25HP ratings, for 240VAC input.
I suppose the alternative would be using a rotary phase converter in order to stick with the cheaper drive (PF525), but I really don't think there'd be any cost savings, plus now there's another failure point.