A 60/60/2 fused disconnect serves a UPS which has and 208V/120V, 1 phase, 3 wire output.
The UPS serves three separate 120V, 12A loads.
Is the total power consumed at the UPS: 120V x 12A = 1,440 VA x 3 = 4,320 VA?
Is the amps seen at the line side of the UPS 4,320 / 208V = 20.7 amps?
The UPS serves three separate 120V, 12A loads.
Is the total power consumed at the UPS: 120V x 12A = 1,440 VA x 3 = 4,320 VA?
Is the amps seen at the line side of the UPS 4,320 / 208V = 20.7 amps?