Single Phase Load Calculation with 3 Phase Service

Merry Christmas
Status
Not open for further replies.

ecampos

New User
Location
PA
Occupation
Controls Engineer
How is the FLA of single phase components calculated when the service is 3 phase? For example with a 480V/3PH service, loads being a 3kW electric heater @ 480V/3PH, and a 1KVA transformer @ 480V/1PH.

Would the total panel FLA be:
( 3000 / (480 * 1.73) ) + ( 1000 / (480 * 1.73) ) = 4.8?
- or -
( 3000 / (480 * 1.73) ) + ( 1000 / 480 ) = 5.7?
 
3000/480= the single phase amps of the heater. Divide the answer by 1.73 to get the 3 phase amps=6.25/1.73=3.6 amps

1kva transformer=1000/480=2.08 amps

3.6A + 2.08A= 5.7A

So you would have 5.7A on two legs of the 480 and 3.6 amps on the other leg if thing are fully loaded
 