Single phase load in 3-phase panel
liaxx2023
utah
Solar Sales Representative
Hey everyone I am having a hard time understanding this calculation. If a single phase load is being fed by a 208V 3phase panel do we calculate the VA by just multiplying the circuit breaker rating to 208V or it should be [breaker rating/1.732] (208V) ?
You would not use the 1.732 factor in the calculation when the load is single phase.
In addition, the load current is (almost) never equal to the circuit breaker rating. If you want actual VA, you need to know the rating of the load.
So the case is there's a 48A single phase continuous load that will be supplied by 3-phase panel 208V as per the problem. When I make a load schedule the demand load of each loads is computed as [60/1.732][208V]? or just [60][208V]?
Don't use the 1.732 as you just quoted infinity as saying.