I had some electric heat strips added on a job which are single phase 208 in a 3 phase panel, when doing a load calc. would you just divide the total va by 208 and not use the 3 phase multiplier since its only tapping 2 phases.
 

KWH

Senior Member
Yes, VA/208V

Sent from my Nexus 5 using Tapatalk

I understand to divide by 208 for branch circuit but for total load on panel would you add those in with everything else and divide by the 359.84 or do that branch separate and add to the rest of the loads for a total panel load.
 

victor.cherkashi

Senior Member
Location
NYC, NY
By dividing total load of panel by 360, you're assuming that all phases are balanced, but usually it's not. By dividing total load by 360, it's gives you estimated Amps on each phase.

Sent from my Nexus 5 using Tapatalk
 

Cow

Senior Member
Location
Eastern Oregon
Occupation
Electrician
The way I was shown and what makes the most sense to me to do load calcs in instances like this, is make a small spreadsheet.

4 columns, one for each phase plus the neutral too.

Then for your rows, you write down your loads. I prefer to show amps on my spreadsheets, but KW's work too. Of course 3 phase loads would show a load across all 3 phases. Single phase across two phases. Pretty straightforward. 25% for largest motor. 125% for continuous loads, lighting, etc.

Add the columns up when you're done and see where your at.

We also use a Fluke logger, it's a little more real world.
 

kwired

Electron manager
Location
NE Nebraska
Thank you. IDR that I’ve ever calculated just that step. Always the whole thing at the same time.

Me neither, but got to thinking and wondering if it wasn't a combination of what most of learned to do in two steps and sure enough it is. I first figured out 208 x 1.732, which is the precision level I usually use and came up with 360.256, and thought where is he getting that, then I though about it and realized it is close enough he may just be using 1.73 level of precision - and then it came out right on.
 
You can calculate all you want, normally, I would allways do a before and after for total load in amps. Knowing that heaters are normally a PF of 1, and the remaining unbalanced loads will also increase your neutral current. Best to Amp Clamp Pre and Post install.

Sent from my LGMP260 using Tapatalk
 