A aberrys Member Location gibson city, illinois, ford county Feb 8, 2018 #1 I have an 230 vac single phase motor with six leads. Amps 11.8@230 vac I'm going to run a 20 amp dual gang breaker and 12 awg thhn wire for my power. Am I required to use overload protection in this situation?
I have an 230 vac single phase motor with six leads. Amps 11.8@230 vac I'm going to run a 20 amp dual gang breaker and 12 awg thhn wire for my power. Am I required to use overload protection in this situation?
ActionDave Chief Moderator Staff member Location Durango, CO, 10 h 20 min from the winged horses. Occupation Licensed Electrician Feb 8, 2018 #2 All motors require overload protection. A single phase motor that size may already have it built in.