ramsy
NoFixNoPay Electric
- Location
- LA basin, CA
- Occupation
- Service Electrician 2020 NEC
If we can't expect one breaker to trip the other two, can two breakers overcome the third?don_resqcapt19 said:In most cases they will not trip the other pole(s).
Are handles listed to tie 3 single-phase breakers anywhere? If a bolted L-L fault --tripping two breakers-- can overcome the third, are we shure a L-L connected ground fault also trips both poles, or just one, which may not overcome the other two handle-tied breakers?