single phase panel from a 3-phase fused disconnect?
donw
Arizona
Hi. I have a tennant improvement that has existing 3-phase SES with class "T" pullout fuses. I need to feed a single phase (3-wire, 208v,120v) panel for x-ray equipment. Is there a problem with just not using one of the phases of the disconnect/fuse?
Thanks,
Don
There is no problem with only using two poles of a three pole device.
In fact, Square D does not make 2-wire fused 480V fused safety switches, their catalog says you need to use a 3-wire device instead.
Are you certain the specs for the x-ray call for (or at least declare to be acceptable) a 208/120 volt single phase supply? Most single phase, dual voltage equipment will call for 240/120, and will not operate properly with 208V