I have a job, Was to wire a 3 phase compressor to a existing panel. I inspected panel and found spacing available.
But when we opened panel. We noticed they used a 3 phase 100 amp breaker, And Step down Transformer and ran a conduit 230 feet with Aluminum xhhw to rear of warehouse.
I presumed this to be a 3 phase panel when the owner asked that he would like compressor next to it. It is a 200 amp single phase.
I am going to explain to owner, That this particular system should be changed to 3 phase. For the Unbalanced nature of the install.
Am I correct in doing so, As far as a hazard is in effect.?