I was wandering if I could get other peoples input of calculating total feeder load demand for single phase ranges - stoves on a three phase 480/208 volt service ?
All ranges equal at 12 KVA each
Here’s what I know:
For multi-occupancy building with 1 range per apartment, calculate the number of apartments and divide by 3
This determines the number of ranges to be placed between phase pairs for load balance
Example 30 apartments / 3 = 10 ranges per pair of phases
Next take 2 (phase legs) x 10 (ranges) = 20 ranges per adjacent phases
Look up table 220.55 column C = 35 kVA for 20 ranges
35,000 VA apparently is the load for adjacent phases and I don’t get the final parts of calculations to determine total load calculation on the three phase service. Also what is the reason for special calculations here?