I have very few details at this point.
The solar contractor is proposing a 1000 amp, 120/240 volt single phase service from the POCO. This will be the path for the future solar plant supporting a facility averaging 3MVA load, 480/277.
My initial reaction is that if they actually do build a solar plant above 250kW, I would want that fed into the POCO through a three phase transformer. The facility should use whatever the solar plant produces and I expect that none would ever be available to be sold back to the POCO.
My concern is that the balance of voltage, currents and harmonics would be disrupted when it doesn't need to be.
Is this a bad idea?