Got another interesting one.
Meter/Main no distribution. After that it feeds a Kohler ATS, then several panels.
Apparently, the electronics in the ATS keep burning out. They want a whole house SPD.
Unfortunately, in the main panel is a 200A main disco, no distribution, no slots for breakers.
Fist useable OCPD for an SPD would be in one of the sub panels after the ATS, and we want to put it before.
I found some Type 1 SPDs made by Eaton that it appears do to need an OCPD, and they are seated for line side of the service entrance, but I've only found them in 3 phase.
I could do a panel change, and install a new 8 space CH panel that has feed-through lugs. That'll probably be my best option.
I don't know as much as I wish I did about SPDs, so what if I did a small panel next the main, say a little 2/4 panel, and put the SPD in there. Does it matter if the panel is "adjacent", electrically, to the main, or would I need the main feed to go through that panel for it to be effective? The SPDs are parallel to the feeders anyway, would it matter if it was in a separate panel?
Meter/Main no distribution. After that it feeds a Kohler ATS, then several panels.
Apparently, the electronics in the ATS keep burning out. They want a whole house SPD.
Unfortunately, in the main panel is a 200A main disco, no distribution, no slots for breakers.
Fist useable OCPD for an SPD would be in one of the sub panels after the ATS, and we want to put it before.
I found some Type 1 SPDs made by Eaton that it appears do to need an OCPD, and they are seated for line side of the service entrance, but I've only found them in 3 phase.
I could do a panel change, and install a new 8 space CH panel that has feed-through lugs. That'll probably be my best option.
I don't know as much as I wish I did about SPDs, so what if I did a small panel next the main, say a little 2/4 panel, and put the SPD in there. Does it matter if the panel is "adjacent", electrically, to the main, or would I need the main feed to go through that panel for it to be effective? The SPDs are parallel to the feeders anyway, would it matter if it was in a separate panel?