onewireatatime
Member
- Location
- California
- Occupation
- Electrician
Hello, I have a residence that is being supplied 120/240 single phase. The actual home will be located 1,100' away from the meter, so we will be using a step up transformer from 240 to 480 and then step back down to from 480 to 120/240 to feed the home. My question is, will i be needing to bond the secondary of the step up transformer that feeds the step down? i will not be using a neutral to feed the step down. I'm concerned of not having a ground fault path in that raceway.
Also, the supply house offered a 240/480 - 120/240 and the manufacture said this type of transformer can be wired backwards to become a step up, if that makes any sense. not sure if any of you guys have done anything similar to this. The Transformer is a ACME TP530233S
Also, the supply house offered a 240/480 - 120/240 and the manufacture said this type of transformer can be wired backwards to become a step up, if that makes any sense. not sure if any of you guys have done anything similar to this. The Transformer is a ACME TP530233S