oldsparky52
Senior Member
- Location
- Wilmington, NC USA
I'm looking at a project that has 3 single phase transformers (480:120/240) to be installed. Each of these transformers will be fed from a 3-phase 480V [FONT=inherit !important][FONT=inherit !important]MDP[/FONT][/FONT]. The loads stated below are the 480V loads feeding the transformer.
Transformer 1 has a calculated load of 270A connected to A&B phases
Transformer 2 has a calculated load of 393A connected to B&C phases
Transformer 3 has a calculated load of 181A connected to C&A phases
The question is what are the calculated loads for A,B,C phases feeding the MDP.
(Please let's not let this go to other questions, I am looking for the proper math for this calculation).
I came across a formula on the "web" and I came up with
A=393
B=577
C=508
I'm not sure I got the correct formula and I'm not sure I implemented it correctly so I'm looking for either confirmation of my calculations or instructions on what the correct answer is and how it is calculated.
Thanks
Transformer 1 has a calculated load of 270A connected to A&B phases
Transformer 2 has a calculated load of 393A connected to B&C phases
Transformer 3 has a calculated load of 181A connected to C&A phases
The question is what are the calculated loads for A,B,C phases feeding the MDP.
(Please let's not let this go to other questions, I am looking for the proper math for this calculation).
I came across a formula on the "web" and I came up with
A=393
B=577
C=508
I'm not sure I got the correct formula and I'm not sure I implemented it correctly so I'm looking for either confirmation of my calculations or instructions on what the correct answer is and how it is calculated.
Thanks