frenchelectrican said:
That reason why most peoples were not really aware with third phase have oddball action sorta like wild leg if you get my point. and that the whole moot point when someone hook up equiment and not aware with single phase load reqirement that part useally catch someone off guard if not paying attetion on this one.
Exactamundo! Treat the third 'synthesized' leg as the high leg on a 4-wire Delta: the third leg is only for 3-phase loads. However, unlike a Delta, you should not try to power a 1-phase line-to-line load using the third leg.
 
We used to see these in small printing shops located in strip stores.
I wouldnt consider a rotary or static phase converter to be something so unusual.
Two wires in, three wires out. Of course it would only be for the equipment it was dedicated to.

Another fun thing to see is a small electric generator on a 480v sewing maching set up only to power a 120v worklight.
 