For your application, I would suggest using a VFD instead of a phase converter. To power it from single-phase power, you simply over-size the converter by 1.7 times the rated output. The VFD takes incoming power and converts it to DC before creating a 3-phase signal. The need for derating is because the input rectifier is not as efficient on single-phase as it is on 3-phase.