Single Phase to Three Phase conversion

Status
Not open for further replies.

funseebee

Member
Location
CA
The existing condition is a single phase system. There are 3-500kcmil & 1-#2(ground) cables in a 3" conduit. The feeder run is overhead and underground from the main switchboard to a power distribution panel at approx. 300 ft.
Now, the plan is to convert it to a three phase system in a very cost effective way.
Is it a Code violation to run a new 1-500kcmil in a separate conduit parallel to the existing feeder run?

Any suggestion? Please help. Thanks. :confused:
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
You cannot run a separate conductor in a separate conduit. You could use the existing feeder as a 3 wire, three phase feeder and install a transformer at the end to create a 4 wire system with a neutral but you may have a problem if the existing grounded conductor has white insulation.
 

Smart $

Esteemed Member
Location
Ohio
...but you may have a problem if the existing grounded conductor has white insulation.
Not if run as a corner grounded delta feed. Depending on the converter type, may have to put a transformer at the source end to get a corner grounded 3? system, though.
 

funseebee

Member
Location
CA
You cannot run a separate conductor in a separate conduit. You could use the existing feeder as a 3 wire, three phase feeder and install a transformer at the end to create a 4 wire system with a neutral but you may have a problem if the existing grounded conductor has white insulation.

Hi,
What do you mean by your statement "you may have a problem if the existing grounded conductor has white insulation"?
Please elaborate. Thanks.:confused:
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
1) What kind of conduit is this? What kind of wire (insulation)?

2) What is the reason for wanting the third phase (more power? three phases for rotating equipment? adding a rectifier?)

3) In the new configuration do you need the neutral?

4) Is the second conduit that you are considering already installed as a spare?

5) What is the insulation color on the currently installed wires?

6) Is this an industrial setting?

-Jon
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Hi,
What do you mean by your statement "you may have a problem if the existing grounded conductor has white insulation"?
Please elaborate. Thanks.:confused:

Article 200 outlines when you can re identify a white conductor. If memory serves me correctly this isn't one of them.

A corner grounded Delta feed would require that the system was already a corner grounded system. Not very likely IMO.
 

hurk27

Senior Member
Article 200 outlines when you can re identify a white conductor. If memory serves me correctly this isn't one of them.

A corner grounded Delta feed would require that the system was already a corner grounded system. Not very likely IMO.

you are correct, you can re-identify a ungrounded color to a white, in a raceway if it is a #6 or larger, but only cable assemblies can you re-identify a white as a un-grounded conductor, no size restrictions.

see 200.3(C):wink:
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
you are correct, you can re-identify a ungrounded color to a white, in a raceway if it is a #6 or larger, but only cable assemblies can you re-identify a white as a un-grounded conductor, no size restrictions.

see 200.3(C):wink:

That's why I said white conductor. If the original single phase installation used white tape on the grounded conductor then it can simply be removed and made into a phase conductor. That would provide a three phase feeder which could feed a transformer which would create the neutral and a three phase, 4 wire setup.
 