100% eff. transformer.
primary is 7200 volt.
2-120 volt loads on leg 1.
first load has 15 ohms of resistance
second load pulls 10 amps
2-120 volt loads on leg 2.
first load pulls 12 amps
second load has 8 ohms of resistance
2-240 volt loads
first load uses 9600 watts
second load uses 4500 watts of power.
I have 3 questions to start out.
first question is what is the current flowing in line 1 with all loads on?
2. what is the current flowing in line 2 with all loads on?
3. what is the current flowing in the secondary with all loads on?
book answers are:
1. 76.75 amps
2. 85.75 amps
3. 81.25 amps
i understand the answers to 1 and 2. the answer to question 3 is my main problem.
to sum all this up my main question is:
answer to question 2 says In line 2 85.75 amps are being pulled with all loads on.
answer to question 3 says 81.25 amps are being pulled in the secondary with all loads on.
how can the whole secondary pull less amps than just line 2 with all loads on?
primary is 7200 volt.
2-120 volt loads on leg 1.
first load has 15 ohms of resistance
second load pulls 10 amps
2-120 volt loads on leg 2.
first load pulls 12 amps
second load has 8 ohms of resistance
2-240 volt loads
first load uses 9600 watts
second load uses 4500 watts of power.
I have 3 questions to start out.
first question is what is the current flowing in line 1 with all loads on?
2. what is the current flowing in line 2 with all loads on?
3. what is the current flowing in the secondary with all loads on?
book answers are:
1. 76.75 amps
2. 85.75 amps
3. 81.25 amps
i understand the answers to 1 and 2. the answer to question 3 is my main problem.
to sum all this up my main question is:
answer to question 2 says In line 2 85.75 amps are being pulled with all loads on.
answer to question 3 says 81.25 amps are being pulled in the secondary with all loads on.
how can the whole secondary pull less amps than just line 2 with all loads on?