Mull,mull982 said:Sorry I forgot the sketch.
For this to happen you need a third point, You can then describe any two points (i.e. the ends of the single coil) in relation to the reference point.mull982 said:In one of the threads I saw the following comment regarding the two legs of a single phase source:
"They both hit zero at the same time, and they both hit peak values at the same time. But one is hitting a positive peak at the same time the other is hitting a negative peak. In other words, when they hit zero together, one is about to go positive and the other is about to go negative. That is what is meant by saying they are in opposition".
The relationship between the two ends of a non-center tapped single coil do not change.....Why are they different if there is only one source, and no tapped nuetral point on the coil?
rattus said:Mull,
Your diagram shows a sine wave starting at time 0. In that case, we can define Vab to have a phase angle of 0. Then, Vba will have a phase angle of 180 degrees.
In fixed phasor form we have,
Vab = 240V @ 0, phasor arrow points to the right
Vba = 240V @ 180, phasor arrow points to the left
Phasor arrows do not move.
Fixed phasors are used in steady state analyses.
In rotating phasor form we have,
vab(t) = 339V*sin(wt)
vba(t) = 339V*sin(wt + 180)
Phasor arrows point away from each other and rotate CCW--one rotation per cycle.
mull982 said:Ok I'm starting to see the vectors Vab and Vba.
I guess what started all of this and whats leading to my confusion, is the vectors diagram I keep drawing which I am getting from this article:
http://www.allaboutcircuits.com/vol_2/chpt_13/9.html
rattus said:I would argue also, that the use of the neutral as a reference is standard procedure in engineering work.
rattus said:Mull, the diagram you reference describes the magnetic field in the motor. Do not confuse this with the phasors which describe the voltages.
jim dungar said:But it can add confusion to circuits that do not contain a neutral, like a single non-center tapped motor or transfromer winding, which are standard circuits.
mull982 said:Ok I see. Is this magnetic field set up by two different stator coils (two poles) or just one coil for these diagrams. If there are stator coils I can see how this diagram works, but am having trouble seeing it through only one coil.
winnie said:Guys, please don't sidetrack Mull's question with a rehash of the argument about inverse versus phase shift in single phase systems. We've already filled hundreds of posts on that topic, and while I am quite willing to go another round or three on the topic, let's do that in another thread
Mull, here is my stab at the 'two vectors' issue:
In the real single phase motor, there is a _single_ changing magnetic field. This magnetic field does not change direction, but continuously changes magnitude, following the AC current waveform in the coil.
Now imagine that you had _two_ rotating magnetic fields, both rotating at the same frequency, but in opposite directions, aligned so that their peaks match up with the orientation of the real magnetic field in the motor, and each with a magnitude half the peak of the real field.
Take the _sum_ of these two "fictional" rotating magnetic fields. This sum will be the real field in the motor. When these two equal magnitude vectors point in opposite directions, the total flux is zero; when they point in the same direction the total flux is maximum, and because they are equal and balanced, the total flux always points along the same axis.
I put fictional in quotes above, because while the _real_ magnetic field has a fixed direction and is simply altering in magnitude, and these component rotating fields seem like a mathematical trick, they are present in a very significant fashion.
If you had some sensor which responded to one of these "fictional" rotating fields more strongly than the other, then rather then seeing the non-rotating balanced sum, that sensor would really 'see' a rotating field.
A squirrel cage rotor spinning in this fluctuating magnetic field would be at different slip relative to the two rotating component fields. Because of the different slip, the two fields will put different torque on the rotor. The rotor is responding differently to the two rotating fields, and thus 'sees' a net rotating field. If the rotor is spinning near synchronous speed for one of these component rotating fields, then it is at very high slip for the other. The net result is that one field will totally dominate the other.
Now when the rotor is exactly stopped, it has the _same_ slip relative to the two fields, and thus does not see a net rotating field. This is why single phase motors are not 'self starting'.
-Jon
winnie said:Sorry about the delay in reply; I spent a bit of time trying to find a good image of a stator winding. What I want to show you is really '3-D', and what I'd love to do is take apart a motor and sketch the thing out by actually pointing to the parts.
When we say 'one coil' we are actually over-simplifying. Virtually no induction motor actually has a _single_ coil, even the simplest 2-pole single phase motor. Instead there are a set of coils of roughly the same orientation. These coils literally _surround_ the rotor.
Here is a good view of a stator: http://www.ewh.ieee.org/soc/es/Nov1997/09/A_DIS1.JPG A 'coil' follows a path _down_ one slot, around the 'end turn' _up_ another slot, around the 'end turn', and back to the first slot. The relative placement of the slots determine the sort of magnetic field structure that the 'winding' will produce.
I found this set of animations: http://www.ece.umn.edu/users/riaz/mrmovies/listmovie.html and clip 8 ("Magnetic field distribution due to single-phase excitation. " does a pretty good job of showing a single phase 2 pole field. The dots at the edge represent the current flow in the slots, as seen edgewise.
Just as an aside: Keep in mind when you look at this that the 'big vector' representing the entire field is a tremendous simplification; what really matters is the distribution of the 'little vectors' representing the flux crossing the gap between rotor and stator; if you stay stuck on the 'big vector' then you will get stuck when you go to '4-pole' motors. (for another time)
A three phase motor has three _sets_ of coils placed at different orientations, each 120 electrical degrees apart. (Electrical degrees means "as measured relative to the magnetic field.") Each of the sets of coils has individual coils which are not at exactly the same angle; but they are treated as a distributed set with a single net angle.
When you single phase a three phase motor, you still have sets of coils operating, just with a somewhat different distribution than in a 'proper' single phase machine.
Phase angle cannot be defined with only two supply terminals. Voltage is measured between two terminals, and phase angle is measured between _two_ voltages. When you single phase a motor, all of the remaining energized coils are energized at the _same_ time; there is no phase angle difference.
-Jon
winnie said:I've no idea what the white dots represent.