Last month we had a single phasing event throughout the campus on our primary side. A few VFD's tripped out, our mechanical equipment without VFD's have phase loss protection and protected themselves properly. The other day though, during the Annual NFPA 25 inspection, we realized that we lost our fire pump controller, more specifically the lead contactor in the pump.
This is a 7 year old Joselyn Clark controller, with two 400A contactors one hooked up to the 65% taps of an autotransformer. Unfortunately for us, Joselyn Clark no longer manufactures pump controllers and the replacement proprietary contactor is now $22,000 for a new one. Needless to say we ordered a newer solid state controller.
Here is my question. How could we have completely melted the plastic seats and scorched the contacts in the contactor during a single phasing event, in a no load condition? The pump was not running during the event. Nobody on the campus believes that the event could have caused the failure, but the pump hasn't ran since it was last checked a month prior and everything was perfect. Also, after the single phasing event, the strip mall across the highway lost multiple pumps/controllers too. Not sure if they failed the same way or not.
Anyone interested in taking a stab at explaining this to me? Hopefully this is the correct thread for this....
This is a 7 year old Joselyn Clark controller, with two 400A contactors one hooked up to the 65% taps of an autotransformer. Unfortunately for us, Joselyn Clark no longer manufactures pump controllers and the replacement proprietary contactor is now $22,000 for a new one. Needless to say we ordered a newer solid state controller.
Here is my question. How could we have completely melted the plastic seats and scorched the contacts in the contactor during a single phasing event, in a no load condition? The pump was not running during the event. Nobody on the campus believes that the event could have caused the failure, but the pump hasn't ran since it was last checked a month prior and everything was perfect. Also, after the single phasing event, the strip mall across the highway lost multiple pumps/controllers too. Not sure if they failed the same way or not.