Single phasing protection of three phase motors

Status
Not open for further replies.
It would seem that it is good practice to always protect a motor from single phasing, and way back in the 70's I worked for a summer designing single phase detection for one of the big electrical equipment manufacturers. But I haven't found any spec that requires it. Is there a requirement by NEC, OSHA, or ? that three phase motors be protected against single phase power input? :confused:
 
Single-phasing

Single-phasing

NEC does not require it. Remember the NEC is developed by NFPA to protect buildings from burning down and costing lives and insurance companies money. Almost every utility has a clause in their service rules that says that they do not promise to have 3-phase power available at all times and that end users are required to install protective equipment to protect motors from single-phasing. Most users never bother and end up burning out the motors. That says something for the generally excellent power service we enjoy in USA.
 
I think there's some stuff in the elevators, escalators, and moving walks codes, but other than that, I haven't seen squat. Naturally, it's on print specs here and there, and in many machine control cabinets.
 
We use a voltage monitor that cost's about 70$ which when voltage on any three legs drop below set value it trips a set of dry contacts and gives us a PLC input. Then we shut down all motors.

Or you could hard wire the start circuit thru such contacts. Money well spent.
 
Voltage monitors can be fooled by phantom regeneration of a missing phase by other rotating equipment (think of a rotary phase converter). The best Phase Loss Monitors are those that are based on current.
 
seems like 3 current transformer rings might serve as a low cost version if someone rigged up a monitor, or you could just buy one. SSAC is one palce I found that sells them.
 