I have incoming service coming into trough that has four service disconnect grouped one location.
I provided one grounding electrode conductor from each service disconnect to common grounding electrode. The common grounding electrode then bonds all grounding electrides present at building.
Inspector came along and said grounding at each service disconnect not allowed and should be at one common location at the trough.
I said 250.64(D)(2) allows this and he said not per NEC 2014 Article 250.24(A)(1). I asked is their any other local amendemnt preventing installation and he said no just 250.24(A)(1).
Am I right or the inspector?
Sent from my SM-G935U using Tapatalk