Im working on a new condo building with several units. On average, a typical demand load per unit is about 28kW and the voltage is 208v coming into the building. These are condos and therefore are subject to change and I would like to leave some capacity for future alterations. Im trying to figure out if it would make more sense / cost effective to bring single phase (or) three phase to the individual dwelling units. These will be fed from a meter center with three phase in, and then three or single phase out depending on conclusion.
So....
28kW @ 208/1 = 135 Amps and I would probably use a 200A service for this because 15 amps of spare capacity (3.1kW) is too close for comfort.
28kW @ 208/3 = 78 Amps and I would probably use a 100A service for this because 22 amps of spare capacity (8kW) is good for spare capacity.
Given all that, do you think it would be more cost effective to use a 200A service @ 208/1 (or) a 100A service @ 208/3? I feel like 3-phase is a better option here due to needing some spare capacity.
Thanks!