As any good electrician will do, I defer to you engineers and then ask..BUT ?
"SIS is not approved for use in conduit."
So why is it listed in the 90C colum of 310.16, (2008)
Table 310.16 Allowable Ampacities of Insulated Conductors Rated 0 Through 2000 Volts, 60?C Through 90?C (140?F Through 194?F), Not More Than Three Current-Carrying Conductors in Raceway, Cable, or Earth (Directly Buried), Based on Ambient Temperature of 30?C (86?F)
So why is it used in all of "MY" SWBD wiring, and , In conduit between detached sections?
Can SIS wire run in a conduit between switchgear and an adjacent protection relay rack? I have a 19" relay rack that sits adjacent to the switchgear it protects. Can I run SIS wire between the relays and the switchgear?
we do it all the time . Utility relay guys abuse sis in ways you can't imagine .
110.3(B) applies...the listing for SIS says for use in switchboards only.Well i see it table 310.13 A application switchboards only i dont see anything stating conduit .
Where in the code does it say no conduit ?
SIS wiring is control wiring and i always thought it was not a issue that control wiring is not a heat factor .
I read the wording in both T310.13 and the UL White book as saying this conductor is suitable for use in switchboards only, but you have correctly quoted the wording.Table 310.13 shows SIS conductor, and under the "Application Provisions" header it says, "Switchboard wiring only". It doen't say "in switchboards only" as one posted here. In my opinion the protective relays are a remote portion of the switchgear, as they are critical to operation and safety. So, to run 20' through a conduit with SIS between the switchgear and relay rack.....code violation or not? Can anyone quote the violation here, or isn't there one? Thanks
SIS ? Indicates a single conductor having thermosetting insulation with no overall covering provided rated 90?C dry, for switchboard wiring only.