Good evening,
Im working on a project where the site lighting went from standard 25' poles which I was feeding with multiple 20A/2P circuit breakers through a contactor. The lighting has been revised to groups of 400W metal halide fixtures which resembles a stadium light. I forget where but I remember reading that I can feed these lights with a breaker rated up to 50A so I was thinking of changing to 50A/2P breakers, does anyone know if this is permitted. I recall reading something about requiring HID circuit breakers however im not sure if this will fit into a standard square d panel.
Thanks!
Im working on a project where the site lighting went from standard 25' poles which I was feeding with multiple 20A/2P circuit breakers through a contactor. The lighting has been revised to groups of 400W metal halide fixtures which resembles a stadium light. I forget where but I remember reading that I can feed these lights with a breaker rated up to 50A so I was thinking of changing to 50A/2P breakers, does anyone know if this is permitted. I recall reading something about requiring HID circuit breakers however im not sure if this will fit into a standard square d panel.