when looking at a site evaluating for an existing testing facility [vehicle testing] with multiple test cells utilizing dyno's / drives I discovered that the incoming pf was pretty low [0.8 based on peak utility demand info] this information was provided from the local utility it turns out the equipment is never utilized to its maximum or near maximum capacity and at the low operating end of the drive the pf gets pretty bad and this can be seen in the overall site pf. just curious what causes the bad pf when the drives operate at the lower end of their operating parameters?
Based on most common vfd drives today, the input PF of vfd drives does not change at all due to what the motor is or is not doing; it remains about .98 at all times. So your .80 PF does not make any sense - yet.
There IS the other kind of PF caused by distortion - like diode front end vfds make; is that what they are referring to?
Are your drives AC? DC? SCR? PWM? Line Regen? We cannnot assume what you have (as I did above)...
See? YOU NEED MORE INFO TO ANSWER THIS. WE NEED MORE INFO TO HELP EXPLAIN IT TOO.
I say you should find out from POCO WHICH PF they refer to as .80. Then you have info to begin addressing it.
At that point, you should tell us what drives, sizes, models, etc, so we can give opinions on solutions.