A site with single utility pad-mount (2500 KVA), CTs and meter at the pad-mount, has an existing 3000A switchgear in one area of the facility. It has 3 other, 100A disconnects in other areas of the facility feeding process loads at other skids/structures. The smaller disconnects are fed from their own conductors off of the secondary of the utility transformer.
- In this case, is the service point the secondary lugs of the xfmr?
- Is each set of underground conductors feeding the 4 service disconnects considered individual sets of service conductors per 230.40?
- Supposing they want to add 3 more skids tapped similarly off of the transformer, is it correct that the six-disconnect rule doesn't apply, since we are dealing with separate structures, even though everything is coming off the same CTs/meter?