I'm going to ask about the Six Hand or Throw rule and how the service conductor is protected from a current overload. I've yet to install a service without a main breaker in the service panel but can see how the Six Hand/Throw rule can come in handy.
I met with an inspector earlier today and asked him "How is the service conductor protected from an overload?" He replied that it was protected by the fuses on the transformer. That may be true for a transformer dedicated to that one service but what if the transformer supplies the whole block ? I'm sure that it's fuses exceed the service conductors of any building on the block.
I'm installing a 200A 3PH service and the client wants a 200A panel on each floor. I don't think that there's enough wire bending room for 200A feeder breakers in something like a SqD NQ panel so a trough under the meter socket and some protected disconnects came to mind but I know that the transformer on the pole serves the building across the street and that it will be the transformer used for my project.
I'm going to ask about the Six Hand or Throw rule and how the service conductor is protected from a current overload. I've yet to install a service without a main breaker in the service panel but can see how the Six Hand/Throw rule can come in handy.
I met with an inspector earlier today and asked him "How is the service conductor protected from an overload?" He replied that it was protected by the fuses on the transformer. That may be true for a transformer dedicated to that one service but what if the transformer supplies the whole block ? I'm sure that it's fuses exceed the service conductors of any building on the block.
I'm installing a 200A 3PH service and the client wants a 200A panel on each floor. I don't think that there's enough wire bending room for 200A feeder breakers in something like a SqD NQ panel so a trough under the meter socket and some protected disconnects came to mind but I know that the transformer on the pole serves the building across the street and that it will be the transformer used for my project.