Section 230.90 Exception 3 says:
Exception No. 3: Two to six circuit breakers or sets of fuses
shall be permitted as the overcurrent device to provide the overload
protection. The sum of the ratings of the circuit breakers
or fuses shall be permitted to exceed the ampacity of the service
conductors, provided the calculated load does not exceed the
ampacity of the service conductors.
This seems to not fall into any of the OCPD exceptions in 240.4. Am I missing something???
Second question: Is there a similar exception for SDS conductors?
Specific situation:
I have a failed 1200A circuit breaker that is on the load side of a 4160/480V transformer. The 1200A CB feeds a panelboard with 6 circuit breakers and the load is WAY less than 1200A. Is there a legal way I can bypass the 1200A CB (it is very old and replacement is not an option)?
As a side note, 240.3 mentions "Services" but it appears to apply to Equipment, not Conductors.
Thanks as always.
Mark
Exception No. 3: Two to six circuit breakers or sets of fuses
shall be permitted as the overcurrent device to provide the overload
protection. The sum of the ratings of the circuit breakers
or fuses shall be permitted to exceed the ampacity of the service
conductors, provided the calculated load does not exceed the
ampacity of the service conductors.
This seems to not fall into any of the OCPD exceptions in 240.4. Am I missing something???
Second question: Is there a similar exception for SDS conductors?
Specific situation:
I have a failed 1200A circuit breaker that is on the load side of a 4160/480V transformer. The 1200A CB feeds a panelboard with 6 circuit breakers and the load is WAY less than 1200A. Is there a legal way I can bypass the 1200A CB (it is very old and replacement is not an option)?
As a side note, 240.3 mentions "Services" but it appears to apply to Equipment, not Conductors.
Thanks as always.
Mark