goldstar
Senior Member
- Location
- New Jersey
- Occupation
- Electrical Contractor
I recently installed a 70 amp, 240 volt, single phase service to an open air building at a day camp. The service started with a 70 amp circuit breaker at the admin bldg. then a 50' run to the outside of the bldg. Once outside it went to an aerial run of about 100' to another out-lying bldg. where I installed a 3-pole, non-fused outdoor disconnect and a mast. From that point there was an existing 2" underground PVC conduit run of about 350' with a concrete vault in between. Once at the new open air bldg. I installed a main-lug breaker panel with 8 active circuits. The inspector tells me that I needed to install a back-fed main breaker because I have more than 6 breakers in the panel. I installed it without argument but I'm confused as to why multi-family dwellings can have a meter enclosure with mains installed for each dwelling and then main lug panels in each unit.
I'm now in the process of upgrading a service at a dwelling that was originally a 2-family and is being converted to a 3-family with a house panel (a 4 meter stack). If the mains are inside the meter enclosure do I now need main breaker panels for each dwelling (there are more than 6 breakers in each panel) ? The breaker panels will be located in a common area of the basement (about 10' away from the meter enclosure) with access to all.
Tnx.
I'm now in the process of upgrading a service at a dwelling that was originally a 2-family and is being converted to a 3-family with a house panel (a 4 meter stack). If the mains are inside the meter enclosure do I now need main breaker panels for each dwelling (there are more than 6 breakers in each panel) ? The breaker panels will be located in a common area of the basement (about 10' away from the meter enclosure) with access to all.
Tnx.