I know this has been discussed ad nauseam, but I want to document this so I don't end up searching this topic for 30 minutes next time it comes up.
Can you legally size conductors based on 80% of a standard breaker?
Example, an industrial location is installing a panelboard with a 400A 80% rated main breaker that currently only has 200A of continuous load.
Do you need to size the feeder conductors to carry 400A (ignore any correction factors for this debate) or can one assume that the breaker should not be loaded to more than 80% of continuous load thus the conductors could be sized to carry 320A?
Can you legally size conductors based on 80% of a standard breaker?