Do disconnects have a make rating? I have a situation where a manufacturer of a 1600A fusible disconnect is saying that the inrush of a 500kva transformer exceeds their switch rating. The disconnect is operating a Gnd-Wye/Gnd-Wye 500kva transformer. The transformer is being used to step up from 120/208 to 277/480. The disconnect is a bolted pressure switch on the 208 side. After operating a few times to power off and on the transformer the center phase contact welded closed. There was no load on the transformer during switching. Also the fuses didn't blow in the disconnect. We were finally able to get it to open after applying manual pressure on the disconnect handle while tripping it. There is now obvious signs of arcing on the middle phase and visible soot. The manufacturer is refusing to replace the disconnect. Any help would be greatly appreciated.