Size light to use on roof of building for parking lot

Status
Not open for further replies.

highpowered

Member
Location
los angeles
Hi Everyone, I'm curious to see what you guys think about what wattage of light fixture I would usse to light up a parking lot. The fixtures would be mounted to the roof of a 3 story building pointing down to the parking lot below. The roof is 150' long and 3 storys high. I was thinking 3-4 300 watt fixtures. The quote will have LED option and high pressure sodium option. the parking lot is 175'x75'. Thanks in advance!1
 
Hi Everyone, I'm curious to see what you guys think about what wattage of light fixture I would usse to light up a parking lot. The fixtures would be mounted to the roof of a 3 story building pointing down to the parking lot below. The roof is 150' long and 3 storys high. I was thinking 3-4 300 watt fixtures. The quote will have LED option and high pressure sodium option. the parking lot is 175'x75'. Thanks in advance!1

A foot candle calculation will be beneficial and let you know exactly what to use. PM for info/details if you're interested.
 
Hi Everyone, I'm curious to see what you guys think about what wattage of light fixture I would usse to light up a parking lot. The fixtures would be mounted to the roof of a 3 story building pointing down to the parking lot below. The roof is 150' long and 3 storys high. I was thinking 3-4 300 watt fixtures. The quote will have LED option and high pressure sodium option. the parking lot is 175'x75'. Thanks in advance!1


If by 300 watt fixtures you are talking quartz halogen lamps - you will get the bid if they want cheap. They will not be happy with how often they need to be relamped.
 
Around here, many towns have a zero-cutoff requirement - no light emitted upward. We would not be able to light a lot that way because the fixtures would need to be aimed at a high angle.

Your vendor should be able to provie a light calculation and advise on the right lights for the job.
 
What would be a good fixture to use?
Anything with an element probably isn't a good idea, and may not even meet local energy efficiency codes. This type of lamp will easily use five times the energy as other types and lamp life will easily be 25% of many other types. You would also need to change lamps maybe twice a year vs every 3-5 years or better
 
Where did you get the .92 footcandles for a parkway? Is that in the NEC

The word "footcandle" does not appear in the NEC. The only code requirements impacting site lighting are any local ordinances on light trespass. The IESNA publishes recommendations for light levels. I refer to them less often since the energy codes have been adopted. Usually nowadays I follow the energy code for watt densities instead. The IECC allows a watt density of 0.06 W/ft2 for parking lots in mixed-use residential areas.
 
Uniformity

Uniformity

Does the owner care about the quality of the lighting? You have fixtures 30 feet in the air and need to throw 75 feet horizontally. A good design is 1fc on average across the entire area. But, you also want to manage the ratio of brightest to dimmest. The parking lot is 13,000 sq ft. At 1fc that is 13,000 lumens. So, if the fixtures were perfect, you need 13,000 lumens of light coming from the fixtures and evenly spread on the parking lot. You need a light with a throw pattern to get the light away from the building, out into the parking lot. A narrow forward throw is needed: this has a wide horizontal spread but a narrow vertical spread. When the fixture is aimed at the middle of the lot (35 ft from the building) you want the spill toward the building and toward the farther edge of the parking lot to be acceptable. A standard flood light or high bay will not work. HPS fixtures, if the color is acceptable, are the most energy efficient inexpensive fixtures. Metal halide are better color but less energy efficient. LED are more energy efficient but pricey.

Warning: if there are paths of egress that cross the parking lot from the building, the fire code light levels must be met. That can be a challenge. In that case, you really want a lighting designer to model the situation and select the number, location, type and size of fixtures. Good luck.
 
What would be a good fixture to use?

1,000 watt metal halides would do okay.


59426_184eecca157a69f829f10ab9214333291d487fba_original_x_323.jpg




I don't like the color of High pressure sodium's..:happyno:
 
Last edited:
Blinding

Blinding

You might get the kind of light levels you want but the glare and distribution from a flood like this may also be unacceptable when mounted on a roof at 30ft up. Anyone looking at the building will be blinded by the glare and unable to see anything in the parking lot.

Consider the characteristics of the Lithonia HFA 400S RN or Lithonia 55 1000M RPN or Lithonia 95 1000M RWH to get the wide but not-high light pattern. I use these fixtures as reference only, many manufacturers make similar fixtures. It is the pattern (5H x 1V) that matters.
 