In a single 3ph motor connection, can I size the MOP by FLA X 2.25 ? It's understood MCA = FLA X 1.25
Last edited:
If you are saying motor over load protection, that is sized 125% of FLA motor nameplate. Unless there are some exception that allows greater than that and I’m not aware of.In a single 3ph motor connection, can I size the MOP by FLA X 2.25 ? It's understood MCA = FLA X 1.25
MOP? I know I'm the silly Brit here but I don't recognise that term. But I'm sure it isn't what we called a Motorised Potentiometer,.........In a single 3ph motor connection, can I size the MOP by FLA X 2.25 ? It's understood MCA = FLA X 1.25
Maximum overcurrent protection that uses in USMOP? I know I'm the silly Brit here but I don't recognise that term. But I'm sure it isn't what we called a Motorised Potentiometer,.........
Copy from factory table of MCA and MOPWhere did the 2.25 number come from?
Maximum overcurrent protectionMOP? I know I'm the silly Brit here but I don't recognise that term. But I'm sure it isn't what we called a Motorised Potentiometer,.........
How do you size MCA and MOP to multi motors. Let me do this if it is correct?If you are saying motor over load protection, that is sized 125% of FLA motor nameplate. Unless there are some exception that allows greater than that and I’m not aware of.
This doesn't look like a single motor. It's difficult to follow but seems to suggest that you need a conductor with an ampacity of not less than 154.3, and a circuit breaker not greater than 175A.Copy from factory table of MCA and MOP
Table 1 – Traditional air conditioner Load Rating MCA Correction Factor MCA Rating MOP Correction Factor MOP Rating
Compressor 1 34.3 125% 42.9 225% 77.2
Compressor 2 34.3 100% 34.3 100% 45.7
Fan Motor 1 13.4 100% 13.4 100% 13.4
Fan Motor 2 10.0 100% 10.0 100% 13.4
Fan Motor 3 10.0 100% 10.0 100% 13.4
Heater 1 25.0 125% 31.2 100% 34.2
Heater 2 12.5 100% 12.5 100% 17.1
Humidifier 12.0 0% 0 0% 0
Total - - 154.3 - 182.4 (175)
Appreciated, thank you.Maximum overcurrent protection
That’s right. MOP is not something you would calculate in the field, MOP is a value calculated by the equipment mfr and put on the equipment nameplate so that you don’t have to do the more complex method kwired described.Are you selecting for a single unit that has all these loads within? If so it should have a nameplate with MCA and MOP for the unit. ...