Two temp trailer, each with it's own 100 amp panel mounted externally. There is an existing 2" pvc feed from 200 amp panel, and this is the only way to get power for eaach panel. Total footage is 100' from source to "sub panels" mounted on outside of trailer. So the existing 2" underground pvc must be able to handle both 100 amp circuits.
Partner and I are arguing over grounding/bonding/sizing of conductors
Driven ground rod at each "sub panel" connected to ground bar at each panel?
6 #2 xhhw( 2- 120/240v circuits) to pull box, then split for each trailer, plus what size of bonding conductor or bonding conductors?
Partner says the 2" conduit to the first pullbox where they split and go to each subpanel only needs (1) #6 bond wire, then spliced and continued in each sperate conduit to each subpanel?
Correct?