could you please explain for the both cases...
240.4(B) Devices Rated 800 Amperes or Less.
The next higher standard overcurrent device rating (above the ampacity of the conductors being protected) shall be permitted to be used, provided all of the following conditions are met:
(1) The conductors being protected are not part of a multioutlet branch circuit supplying receptacles for cord-and-plug-connected portable loads.
(2) The ampacity of the conductors does not correspond with the standard ampere rating of a fuse or a circuit breaker without overload trip adjustments above its rating (but that shall be permitted to have other trip or rating adjustments).
(3) The next higher standard rating selected does not exceed 800 amperes.
Please can we discuss 1 & 2
Many thanks.........clear nowNot sure what there is to discuss.
What part of the text do you not understand ?
In (1) you can't go to the next size up in the conditions stated. For example if you derate #12s to a amperage less than 20 and you are feeding multiple receptacle outlets on a multi-wire branch circuit you can't upsize to a 20 amp breaker.
In (2) you can't go above the next "standard size" OCP from 240.6.
For example if your derated factor is 69, or 70, you can't go beyond 70 since that's a standard size.