We check the nec about the size of the conductors (output inverter) inside banks conduits (pvc) in the trenches. We have in the same trench some pvc conduits with different circuits (some ac, sometimes dc), and we understood that:
- you must multiply amps*1,25
- you must to check the size in table B.310 (depends of the number of conduits) and use the factor temperature to adjust it.
- or Easier- use one program as Ampcal, or other
We check that really you need a very, very big size of cable using the nec.....
Is this the correct way to do it?
Why in the B.310 there aren´t 90º cable temperature?, (conductor temperature 75º)
Is there a free computer program to do it?
Regards