Feeding a wet bar outside, with a few recps for general use, then using it to feed a pool with 2 pool pumps fiquring them to be 18-20 amps each couldnt get a stright answer from the pool guy, 1 wet niche light and outlets for salt generator and convience outlets.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Calculate the total connected load using the heaviest loads you are aware of and add a little for a buffer, I would probably go about 25 to 50 percent over.

Roger
 

suemarkp

Senior Member
Location
Kent, WA
Occupation
Retired Engineer
The pool pumps should not be much over 10 to 12 amps at 240V (circulation pump should be 1 HP or less, a spa bubble pump may be 2 HP). Two 120V pumps works out the same as two pumps wired for 240V. The light could be up to 500W. The salt chlorinator is almost nothing. So a calculated load of 30A would probably cover the fixed equipment. I'd add 15A to cover convenience outlets. Or plan for a heat pump which could have an MCA up to 35.

So a 60A feeder should be plenty for no heat pump, 70A to 100A if a heat pump gets added. Gas heaters need minimal power.
 