Section 250-50 (99NEC) says "an unspliced GEC shall be permitted to be run to any convenient grounding electrode available in the grounding electrode system or to one or more grounding electrodes individually. It shall be sized for the largest GEC required among all the electrodes connected to it."
Section 250-66(a) says connections to made electrodes as permitted in 250-52(c) or (d) shall not be required to be larger than #6 copper.
Does this mean if you have a water pipe, ground rods or rebar you must use #4 (200A service) to all of them if it is one continuous GEC?
And if you run separate GECs does it mean you can run a #4 to the water pipe and a separate #6 from the buss to the rods or rebar?
Could this be why I only see Cadweld one shots for #6?
I am not sure if rebar qualifies as a "made electrode"
Thanks for any help.
Brian
Section 250-66(a) says connections to made electrodes as permitted in 250-52(c) or (d) shall not be required to be larger than #6 copper.
Does this mean if you have a water pipe, ground rods or rebar you must use #4 (200A service) to all of them if it is one continuous GEC?
And if you run separate GECs does it mean you can run a #4 to the water pipe and a separate #6 from the buss to the rods or rebar?
Could this be why I only see Cadweld one shots for #6?
I am not sure if rebar qualifies as a "made electrode"
Thanks for any help.
Brian